And if anyone can explain the whole power correction factor thing, I'm all ears...no wait, eyes.
![Laughing :lol:](./images/smilies/icon_lol.gif)
Thanks guys.
Here's both the 350 & 250 per manual req's:
Very good point, Steve. That's a real common issue with high draw equipment. Under heavy load conditions, the 60 Hz frequency of the AC current will literally vibrate the set screws away from the wires and cause the connection to loosen marginally. This results in higher resistance and heating.Otto Nobedder wrote:dunkster,
A couple of things I'd look at before modifying anything...
Starting at the machine (unplugged, of course), open the connection panel and inspect the direct input connections. Do you see discoloration (brown or black) where the wires are screwed to the input board? Clean them, and retighten them.
Break down the plug that goes to the wall outlet, and check for the same condition.
With the breaker CONFIRMED off, check the same condition inside the wall outlet.
These issues are remarkably common.
While inspecting the wall outlet, check the condition of the insulation. If the insulation is cracked/damaged, it's a sign of overheating in the wall wire run, and a sign of hazard.
This next step is riskier, so don't do it unless you're qualified, and that is to pull the cover off the breaker box and make the same inspection where the wires come out of the breaker, as well as the neutral and ground wires at their respective busses. Also, look at where the main feed wires attach to the buss bars (but don't mess with these... that's "licensed electrician" work).
Steve S